Many (?most) charger/inverter combination units have the AC and DC grounds connected to the case which is (by ABYC standards) connected to the bonding system.  This is contrary to the Amel system in which DC grounded to the negative battery pole, AC is grounded back to the boat's AC ground, and the bonding system is kept isolated from the electrical systems.
Before I understood this, I added a Sterling charger/inverter which was grounded to the bonding system.  A fault in the inverter occurred and a current leak destroyed the zincs and the prop shaft.

Someone posted here that Amel doesn't put combination charger/Inverters in their boats for this reason.

Be very sure you understand the Amel grounding and bonding systems before you add a charger/inverter.

Kent
SM 243
Kristy


On Nov 15, 2015, at 6:22 PM, ms42phantom54@... [amelyachtowners] <amelyachtowners@...> wrote:

 

I have the same charger configuration, but one is a Dolphin and the other a Charles. Have you tried to use 120V/60 Hz shore power?


Great idea on the charger and inverter setup. I am assuming you will have the charger in line prior to the inverter, as I do not think the combi unit will allow for frequency conversion in a single unit. How do you plan to connect?

What is the rating of your circuit breaker in the lazarette?

Thanks,
Jamie Wendell
s/v Phantom


James Wendell <ms42phantom54@...>
 

Thanks for the advice Kent. I understand the ABYC standards but have yet to fully understand the Amel installation. Your advice is helpful.
Hopefully, I will get it as I upgrade over the winter.
Jamie
s/v Phantom



On Sunday, November 15, 2015 7:57 PM, "Kent Robertson karkauai@... [amelyachtowners]" wrote:


 
Many (?most) charger/inverter combination units have the AC and DC grounds connected to the case which is (by ABYC standards) connected to the bonding system.  This is contrary to the Amel system in which DC grounded to the negative battery pole, AC is grounded back to the boat's AC ground, and the bonding system is kept isolated from the electrical systems.
Before I understood this, I added a Sterling charger/inverter which was grounded to the bonding system.  A fault in the inverter occurred and a current leak destroyed the zincs and the prop shaft.

Someone posted here that Amel doesn't put combination charger/Inverters in their boats for this reason.

Be very sure you understand the Amel grounding and bonding systems before you add a charger/inverter.

Kent
SM 243
Kristy


On Nov 15, 2015, at 6:22 PM, ms42phantom54@... [amelyachtowners] <amelyachtowners@...> wrote:

 
I have the same charger configuration, but one is a Dolphin and the other a Charles. Have you tried to use 120V/60 Hz shore power?

Great idea on the charger and inverter setup. I am assuming you will have the charger in line prior to the inverter, as I do not think the combi unit will allow for frequency conversion in a single unit. How do you plan to connect?

What is the rating of your circuit breaker in the lazarette?

Thanks,
Jamie Wendell
s/v Phantom



Wolfgang Weber <webercardio@...>
 

For your Information. 
This is the answer from Mastervolt concerning the Installation of charger/inverter on Amel 54

"The AC is not connected to the DC terminals inside, the DC is floating to the housing.
however, the AC input is not galphanic isolated from the shore, for this you need a isolation transformer, and create your own ships ground in your boat.
the combi Ultra has an option to switch on a ground relay, this means the neutral in AC output will be connected to the ground in inverter mode automatically. in charger mode (this means there is a AC input like a shore connection, then this relay will be deactivated, because theoretical, the hot and neutral line can be swapped, and you don't want the hot line to be connected to the ground.
our high frequency isolation transformer is 88000355 mass GI 3,5
http://www.mastervolt.com/products/mass-gi/mass-gi-35-kva-16a-lightweight/

hope this helps,

best regards, 
Edwin van der Kroon"
 
Any comment ?  Wolfgang Weber SY ELISE  Amel 54 # 162



James Wendell <ms42phantom54@...>
 

That definitely helps. So in your case all shore power feeds through the Mass GI 3.5, presumably protected by a 16A circuit breaker in the lazarette? Is that the size breaker you have?

I have a 32A breaker in the lazarette, which is too large for the 4mm2 wire Amel installed, and it would not safely protect that size isolation transformer.

I plan to change that to a 16A breaker and use a similarly-sized isolation transformer like yours (I am using the Victron 3.6 unit). I just want to be sure that the breaker doesn't trip all the time if AC loads exceed the 16 amps permitted.

Thanks,
Jamie Wendell
s/v Phantom Amel 54



On Tuesday, November 17, 2015 8:29 AM, "Wolfgang Weber webercardio@... [amelyachtowners]" wrote:


 
For your Information. 
This is the answer from Mastervolt concerning the Installation of charger/inverter on Amel 54

"The AC is not connected to the DC terminals inside, the DC is floating to the housing.
however, the AC input is not galphanic isolated from the shore, for this you need a isolation transformer, and create your own ships ground in your boat.
the combi Ultra has an option to switch on a ground relay, this means the neutral in AC output will be connected to the ground in inverter mode automatically. in charger mode (this means there is a AC input like a shore connection, then this relay will be deactivated, because theoretical, the hot and neutral line can be swapped, and you don't want the hot line to be connected to the ground.
our high frequency isolation transformer is 88000355 mass GI 3,5
http://www.mastervolt.com/products/mass-gi/mass-gi-35-kva-16a-lightweight/

hope this helps,

best regards, 
Edwin van der Kroon"
 
Any comment ?  Wolfgang Weber SY ELISE  Amel 54 # 162





Alan Leslie
 

If you install a 16A breaker and the loads exceed 16A then the breaker will trip.
Alan
Elyse SM437


Bill & Judy Rouse <yahoogroups@...>
 

Jaimie,

I think that you are incorrect on required wire size. How did you calculate that it is wrong? Based on: Wire Circular mils =2 x ρ x I x L / (%Allowable Voltage drop of source voltage) 

4mm = 6 gauge...and 6 gauge is adequate for 230VAC 50htz for 200+ foot length at 3%Allowable Voltage drop.

Is it possible that you have made a mistake? Or, is it possible that your calculations of wire size are based on 110VAC common to the USA?

Also, I would assume that if Amel installed a 16 amp breaker in the lazarette that they would have used 16 amps for a reason...maybe because the vast majority of the 230VAC 50htz shore power connection in Europe and around the world happen to be 16 amp. There are some marinas with a 32 amp option, but not many. So, it is highly likely that the 16 amp breaker was intentional. We happen to be plugged into 230VAC 50htz 32 amp shore power now, but in this new marina, the 32 amp plug that we are using is the only one on our pontoon...30 other boats are plugged into 16 amps.

A word of advice to you. The last person you should doubt in terms of Amel systems design is Amel. And the last thing that you want to do with an Amel is to Un-Amel your Amel.

Also, I sent you a private message.

Bill
BeBe #387



On Tue, Nov 17, 2015 at 4:24 PM, James Wendell ms42phantom54@... [amelyachtowners] <amelyachtowners@...> wrote:

 

That definitely helps. So in your case all shore power feeds through the Mass GI 3.5, presumably protected by a 16A circuit breaker in the lazarette? Is that the size breaker you have?

I have a 32A breaker in the lazarette, which is too large for the 4mm2 wire Amel installed, and it would not safely protect that size isolation transformer.

I plan to change that to a 16A breaker and use a similarly- sized isolation transformer like yours (I am using the Victron 3.6 unit). I just want to be sure that the breaker doesn't trip all the time if AC loads exceed the 16 amps permitted.

Thanks,
Jamie Wendell
s/v Phantom Amel 54



On Tuesday, November 17, 2015 8:29 AM, "Wolfg ang Weber webercardio@... [amelyachtowners]" <amelyachtowners@...> wrote:


 
For your Information. 
This is the answer from Mastervolt concerning the Installation of charger/inverter on Amel 54

"The AC is not connected to the DC terminals inside, the DC is floating to the housing.
however, the AC input is not galphanic isolated from the shore, for this you need a isolation transformer, and create your own ships ground in your boat.
the combi Ultra has an option to switch on a ground relay, this means the neutral in AC output will be connected to the ground in inverter mode automatically. in charger mode (this means there is a AC input like a shore connection, then this relay will be deactivated, because theoretical, the hot and neutral line can be swapped, and you don't want the hot line to be connected to the ground.
our high frequency isolation transformer is 88000355 mass GI 3,5http://www.mastervolt.com/products/mass-gi/mass-gi-35-kva-16a-lightweight/

hope this helps,

best regards, 
Edwin van der Kroon"
 
Any comment ?  Wolfgang Weber SY ELISE  Amel 54 # 162






James Wendell <ms42phantom54@...>
 

Bill, thanks for the feedback. Trust me, I am not trying to question what Amel did, as I am sure they have been installing safe and effective electrical systems in their boats. And I also agree that I do not want to "de-Amel" my boat. I like it essentially the way it is.

But I do have some concerns that my Amel 54 may not be configured as Amel intended, and what I have is definitely not safe. I was hoping to see what others have in their shore power systems to see if I have the right setup. Right now I have a single 32A/230V Hubbel shore power inlet coupled to a 32A/230V circuit breaker in the lazarette feeding my shore power line to the automatic transfer switch in the engine room. The Amel electrical schematics I have indicate there should be a 16A/230V breaker for the 50Hz feeder and also a 32A breaker for a 120V/60Hz feeder with a step-up transformer. I do not have the 16A breaker or the transformer. I am concerned about the possibility that someone may connect my shore power inlet to a 230V or 240V connection (which is what you have to do of course whether in Europe or the US) but then try to run everything in the boat. That would overload my 4mm2 wiring.

I certainly am not immune to making mistakes, but I do think I am looking at this correctly. I am an electrical engineer, so right or wrong I have based my shore power assessments on US National Electrical Code rules. Your approach to determining wire size based on voltage and voltage drop also can be used, but is only really appropriate for DC wiring and not higher voltage AC systems (whether they are 120V or 230V), where voltage drop is not a concern in a house or boat. Voltage drop is only important if you are looking at DC circuits (where we are dealing with 12 or 24 volts).

Respectfully, I must also point out a few issues with your numbers. 4mm2, commonly available in Europe, is a cross-sectional measurement of the wire and not the diameter or circumference. It is the equivalent of a US Wire Gauge Size 11 per the conversion tables. I can see how you might have equated it to a 6 AWG. Since 11 gauge wire is not commonly available in the US, you would have to use 12 gauge wire to be safe.

Current through the wire is the issue and not voltage or frequency. 12 gauge wire (or 4mm2) on any AC circuit (less than 600 volts) is good for up to a 20A breaker and a maximum of 16 amps of continuous current at either 120V or 230V. If you connect a European 230V (or US 240V) power source to a 32A breaker (as I have), the breaker would allow a huge current (up to about 30 amps before tripping) to pass through my 4mm2 wire. In order to handle that much current, I would need to replace the wiring with 6mm2 wire (or 10 AWG in the US). i do not want to do that, as I agree with you that Amel clearly planned for 4mm2 wiring on the 230V/50Hz shore power feeder, and hence the rationale for a 16A circuit breaker. Also I think you are correct that the vast majority of power systems available throughout Europe are indeed 16A rather than 32A.

Those are the reasons why I think the circuit breaker I have is wrong and I should degrade it to 16 amps at 230V. Of course, that would limit my power capacity, but I think that is what Amel would have installed. What size shore power connector and circuit breaker do you have?

Thanks,
Jamie Wendell
s/v Phantom Amel 54



On Wednesday, November 18, 2015 3:59 AM, "'Bill & Judy Rouse' yahoogroups@... [amelyachtowners]" wrote:


 
Jaimie,

I think that you are incorrect on required wire size. How did you calculate that it is wrong? Based on: Wire Circular mils =2 x ρ x I x L / (%Allowable Voltage drop of source voltage) 

4mm = 6 gauge...and 6 gauge is adequate for 230VAC 50htz for 200+ foot length at 3%Allowable Voltage drop.

Is it possible that you have made a mistake? Or, is it possible that your calculations of wire size are based on 110VAC common to the USA?

Also, I would assume that if Amel installed a 16 amp breaker in the lazarette that they would have used 16 amps for a reason...maybe because the vast majority of the 230VAC 50htz shore power connection in Europe and around the world happen to be 16 amp. There are some marinas with a 32 amp option, but not many. So, it is highly likely that the 16 amp breaker was intentional. We happen to be plugged into 230VAC 50htz 32 amp shore power now, but in this new marina, the 32 amp plug that we are using is the only one on our pontoon...30 other boats are plugged into 16 amps.

A word of advice to you. The last person you should doubt in terms of Amel systems design is Amel. And the last thing that you want to do with an Amel is to Un-Amel your Amel.

Also, I sent you a private message.

Bill
BeBe #387



On Tue, Nov 17, 2015 at 4:24 PM, James Wendell ms42phantom54@... [amelyachtowners] <amelyachtowners@...> wrote:

 
That definitely helps. So in your case all shore power feeds through the Mass GI 3.5, presumably protected by a 16A circuit breaker in the lazarette? Is that the size breaker you have?

I have a 32A breaker in the lazarette, which is too large for the 4mm2 wire Amel installed, and it would not safely protect that size isolation transformer.

I plan to change that to a 16A breaker and use a similarly- sized isolation transformer like yours (I am using the Victron 3.6 unit). I just want to be sure that the breaker doesn't trip all the time if AC loads exceed the 16 amps permitted.

Thanks,
Jamie Wendell
s/v Phantom Amel 54



On Tuesday, November 17, 2015 8:29 AM, "Wolfg ang Weber webercardio@... [amelyachtowners]" <amelyachtowners@...> wrote:


 
For your Information. 
This is the answer from Mastervolt concerning the Installation of charger/inverter on Amel 54

"The AC is not connected to the DC terminals inside, the DC is floating to the housing.
however, the AC input is not galphanic isolated from the shore, for this you need a isolation transformer, and create your own ships ground in your boat.
the combi Ultra has an option to switch on a ground relay, this means the neutral in AC output will be connected to the ground in inverter mode automatically. in charger mode (this means there is a AC input like a shore connection, then this relay will be deactivated, because theoretical, the hot and neutral line can be swapped, and you don't want the hot line to be connected to the ground.
our high frequency isolation transformer is 88000355 mass GI 3,5http://www.mastervolt.com/products/mass-gi/mass-gi-35-kva-16a-lightweight/

hope this helps,

best regards, 
Edwin van der Kroon"
 
Any comment ?  Wolfgang Weber SY ELISE  Amel 54 # 162








Andrew & Kate Lamb
 

We have a total run of somewhere between 15-20 meters (internal cabling + shore power cable)  of twin and earth 4mm2 cross section double insulated cable from the shore power to the 32A circuit breaker in the engine room, then onto the 7.5KW rated isolation transformer. All the online and offline calculators/calculations that I have done seem to suggest that this is adequate.

 

Andrew

 

Ronpische

SM2k 472

Canet en Roussillion, France

 

 

 

From: amelyachtowners@... [mailto:amelyachtowners@...]
Sent: Wednesday, November 18, 2015 3:23 PM
To: amelyachtowners@...
Subject: Re: [Amel Yacht Owners] Re: Shore Power Configuration

 

 

Bill, thanks for the feedback. Trust me, I am not trying to question what Amel did, as I am sure they have been installing safe and effective electrical systems in their boats. And I also agree that I do not want to "de-Amel" my boat. I like it essentially the way it is.

 

But I do have some concerns that my Amel 54 may not be configured as Amel intended, and what I have is definitely not safe. I was hoping to see what others have in their shore power systems to see if I have the right setup. Right now I have a single 32A/230V Hubbel shore power inlet coupled to a 32A/230V circuit breaker in the lazarette feeding my shore power line to the automatic transfer switch in the engine room. The Amel electrical schematics I have indicate there should be a 16A/230V breaker for the 50Hz feeder and also a 32A breaker for a 120V/60Hz feeder with a step-up transformer. I do not have the 16A breaker or the transformer. I am concerned about the possibility that someone may connect my shore power inlet to a 230V or 240V connection (which is what you have to do of course whether in Europe or the US) but then try to run everything in the boat. That would overload my 4mm2 wiring.

 

I certainly am not immune to making mistakes, but I do think I am looking at this correctly. I am an electrical engineer, so right or wrong I have based my shore power assessments on US National Electrical Code rules. Your approach to determining wire size based on voltage and voltage drop also can be used, but is only really appropriate for DC wiring and not higher voltage AC systems (whether they are 120V or 230V), where voltage drop is not a concern in a house or boat. Voltage drop is only important if you are looking at DC circuits (where we are dealing with 12 or 24 volts).

 

Respectfully, I must also point out a few issues with your numbers. 4mm2, commonly available in Europe, is a cross-sectional measurement of the wire and not the diameter or circumference. It is the equivalent of a US Wire Gauge Size 11 per the conversion tables. I can see how you might have equated it to a 6 AWG. Since 11 gauge wire is not commonly available in the US, you would have to use 12 gauge wire to be safe.

 

Current through the wire is the issue and not voltage or frequency. 12 gauge wire (or 4mm2) on any AC circuit (less than 600 volts) is good for up to a 20A breaker and a maximum of 16 amps of continuous current at either 120V or 230V. If you connect a European 230V (or US 240V) power source to a 32A breaker (as I have), the breaker would allow a huge current (up to about 30 amps before tripping) to pass through my 4mm2 wire. In order to handle that much current, I would need to replace the wiring with 6mm2 wire (or 10 AWG in the US). i do not want to do that, as I agree with you that Amel clearly planned for 4mm2 wiring on the 230V/50Hz shore power feeder, and hence the rationale for a 16A circuit breaker. Also I think you are correct that the vast majority of power systems available throughout Europe are indeed 16A rather than 32A.

 

Those are the reasons why I think the circuit breaker I have is wrong and I should degrade it to 16 amps at 230V. Of course, that would limit my power capacity, but I think that is what Amel would have installed. What size shore power connector and circuit breaker do you have?

 

Thanks,

Jamie Wendell

s/v Phantom Amel 54

 

 

On Wednesday, November 18, 2015 3:59 AM, "'Bill & Judy Rouse' yahoogroups@... [amelyachtowners]" <amelyachtowners@...> wrote:

 

 

Jaimie,

 

I think that you are incorrect on required wire size. How did you calculate that it is wrong? Based on: Wire Circular mils =2 x ρ x I x L / (%Allowable Voltage drop of source voltage) 

 

4mm = 6 gauge...and 6 gauge is adequate for 230VAC 50htz for 200+ foot length at 3%Allowable Voltage drop.

 

Is it possible that you have made a mistake? Or, is it possible that your calculations of wire size are based on 110VAC common to the USA?

Also, I would assume that if Amel installed a 16 amp breaker in the lazarette that they would have used 16 amps for a reason...maybe because the vast majority of the 230VAC 50htz shore power connection in Europe and around the world happen to be 16 amp. There are some marinas with a 32 amp option, but not many. So, it is highly likely that the 16 amp breaker was intentional. We happen to be plugged into 230VAC 50htz 32 amp shore power now, but in this new marina, the 32 amp plug that we are using is the only one on our pontoon...30 other boats are plugged into 16 amps.

 

A word of advice to you. The last person you should doubt in terms of Amel systems design is Amel. And the last thing that you want to do with an Amel is to Un-Amel your Amel.

 

Also, I sent you a private message.

 

Bill

BeBe #387

 

 

 

On Tue, Nov 17, 2015 at 4:24 PM, James Wendell ms42phantom54@... [amelyachtowners] <amelyachtowners@...> wrote:

 

That definitely helps. So in your case all shore power feeds through the Mass GI 3.5, presumably protected by a 16A circuit breaker in the lazarette? Is that the size breaker you have?

 

I have a 32A breaker in the lazarette, which is too large for the 4mm2 wire Amel installed, and it would not safely protect that size isolation transformer.

 

I plan to change that to a 16A breaker and use a similarly- sized isolation transformer like yours (I am using the Victron 3.6 unit). I just want to be sure that the breaker doesn't trip all the time if AC loads exceed the 16 amps permitted.

 

Thanks,

Jamie Wendell

s/v Phantom Amel 54

 

 

On Tuesday, November 17, 2015 8:29 AM, "Wolfg ang Weber webercardio@... [amelyachtowners]" <amelyachtowners@...> wrote:

 

 

For your Information. 

This is the answer from Mastervolt concerning the Installation of charger/inverter on Amel 54

"The AC is not connected to the DC terminals inside, the DC is floating to the housing.
however, the AC input is not galphanic isolated from the shore, for this you need a isolation transformer, and create your own ships ground in your boat.
the combi Ultra has an option to switch on a ground relay, this means the neutral in AC output will be connected to the ground in inverter mode automatically. in charger mode (this means there is a AC input like a shore connection, then this relay will be deactivated, because theoretical, the hot and neutral line can be swapped, and you don't want the hot line to be connected to the ground.
our high frequency isolation transformer is 88000355 mass GI 3,5http://www.mastervolt.com/products/mass-gi/mass-gi-35-kva-16a-lightweight/

hope this helps,

best regards, 
Edwin van der Kroon"

 

Any comment ?  Wolfgang Weber SY ELISE  Amel 54 # 162

 

 

 

 


James Wendell <ms42phantom54@...>
 

Thanks Andrew, I checked the European wire manufacturers out there and they all seem to indicate that 4mm2 wire is good for up to 32A single phase, so I think you are correct on adequacy in design. I think the US NEC is just more conservative, hence my concern.

I will retain my 32A breaker, but I still would like to find out why my Amel factory electrical schematics indicate a 16 amp 230V circuit breaker. It seems you have a 32A breaker, as do I.

What shore power inlet breaker rating is shown on your Amel drawings?

Thanks,
Jamie



On Wednesday, November 18, 2015 9:46 AM, "Andrew Lamb andrew.lamb@... [amelyachtowners]" wrote:


 
We have a total run of somewhere between 15-20 meters (internal cabling + shore power cable)  of twin and earth 4mm2 cross section double insulated cable from the shore power to the 32A circuit breaker in the engine room, then onto the 7.5KW rated isolation transformer. All the online and offline calculators/calculations that I have done seem to suggest that this is adequate.
 
Andrew
 
Ronpische
SM2k 472
Canet en Roussillion, France
 
 
 

From: amelyachtowners@... [mailto:amelyachtowners@...]
Sent: Wednesday, November 18, 2015 3:23 PM
To: amelyachtowners@...
Subject: Re: [Amel Yacht Owners] Re: Shore Power Configuration
 
 
Bill, thanks for the feedback. Trust me, I am not trying to question what Amel did, as I am sure they have been installing safe and effective electrical systems in their boats. And I also agree that I do not want to "de-Amel" my boat. I like it essentially the way it is.
 
But I do have some concerns that my Amel 54 may not be configured as Amel intended, and what I have is definitely not safe. I was hoping to see what others have in their shore power systems to see if I have the right setup. Right now I have a single 32A/230V Hubbel shore power inlet coupled to a 32A/230V circuit breaker in the lazarette feeding my shore power line to the automatic transfer switch in the engine room. The Amel electrical schematics I have indicate there should be a 16A/230V breaker for the 50Hz feeder and also a 32A breaker for a 120V/60Hz feeder with a step-up transformer. I do not have the 16A breaker or the transformer. I am concerned about the possibility that someone may connect my shore power inlet to a 230V or 240V connection (which is what you have to do of course whether in Europe or the US) but then try to run everything in the boat. That would overload my 4mm2 wiring.
 
I certainly am not immune to making mistakes, but I do think I am looking at this correctly. I am an electrical engineer, so right or wrong I have based my shore power assessments on US National Electrical Code rules. Your approach to determining wire size based on voltage and voltage drop also can be used, but is only really appropriate for DC wiring and not higher voltage AC systems (whether they are 120V or 230V), where voltage drop is not a concern in a house or boat. Voltage drop is only important if you are looking at DC circuits (where we are dealing with 12 or 24 volts).
 
Respectfully, I must also point out a few issues with your numbers. 4mm2, commonly available in Europe, is a cross-sectional measurement of the wire and not the diameter or circumference. It is the equivalent of a US Wire Gauge Size 11 per the conversion tables. I can see how you might have equated it to a 6 AWG. Since 11 gauge wire is not commonly available in the US, you would have to use 12 gauge wire to be safe.
 
Current through the wire is the issue and not voltage or frequency. 12 gauge wire (or 4mm2) on any AC circuit (less than 600 volts) is good for up to a 20A breaker and a maximum of 16 amps of continuous current at either 120V or 230V. If you connect a European 230V (or US 240V) power source to a 32A breaker (as I have), the breaker would allow a huge current (up to about 30 amps before tripping) to pass through my 4mm2 wire. In order to handle that much current, I would need to replace the wiring with 6mm2 wire (or 10 AWG in the US). i do not want to do that, as I agree with you that Amel clearly planned for 4mm2 wiring on the 230V/50Hz shore power feeder, and hence the rationale for a 16A circuit breaker. Also I think you are correct that the vast majority of power systems available throughout Europe are indeed 16A rather than 32A.
 
Those are the reasons why I think the circuit breaker I have is wrong and I should degrade it to 16 amps at 230V. Of course, that would limit my power capacity, but I think that is what Amel would have installed. What size shore power connector and circuit breaker do you have?
 
Thanks,
Jamie Wendell
s/v Phantom Amel 54
 
 
On Wednesday, November 18, 2015 3:59 AM, "'Bill & Judy Rouse' yahoogroups@... [amelyachtowners]" <amelyachtowners@...> wrote:
 
 
Jaimie,
 
I think that you are incorrect on required wire size. How did you calculate that it is wrong? Based on: Wire Circular mils =2 x ρ x I x L / (%Allowable Voltage drop of source voltage) 
 
4mm = 6 gauge...and 6 gauge is adequate for 230VAC 50htz for 200+ foot length at 3%Allowable Voltage drop.
 
Is it possible that you have made a mistake? Or, is it possible that your calculations of wire size are based on 110VAC common to the USA?

Also, I would assume that if Amel installed a 16 amp breaker in the lazarette that they would have used 16 amps for a reason...maybe because the vast majority of the 230VAC 50htz shore power connection in Europe and around the world happen to be 16 amp. There are some marinas with a 32 amp option, but not many. So, it is highly likely that the 16 amp breaker was intentional. We happen to be plugged into 230VAC 50htz 32 amp shore power now, but in this new marina, the 32 amp plug that we are using is the only one on our pontoon...30 other boats are plugged into 16 amps.
 
A word of advice to you. The last person you should doubt in terms of Amel systems design is Amel. And the last thing that you want to do with an Amel is to Un-Amel your Amel.
 
Also, I sent you a private message.
 
Bill
BeBe #387
 
 
 
On Tue, Nov 17, 2015 at 4:24 PM, James Wendell ms42phantom54@... [amelyachtowners] <amelyachtowners@...> wrote:
 
That definitely helps. So in your case all shore power feeds through the Mass GI 3.5, presumably protected by a 16A circuit breaker in the lazarette? Is that the size breaker you have?
 
I have a 32A breaker in the lazarette, which is too large for the 4mm2 wire Amel installed, and it would not safely protect that size isolation transformer.
 
I plan to change that to a 16A breaker and use a similarly- sized isolation transformer like yours (I am using the Victron 3.6 unit). I just want to be sure that the breaker doesn't trip all the time if AC loads exceed the 16 amps permitted.
 
Thanks,
Jamie Wendell
s/v Phantom Amel 54
 
 
On Tuesday, November 17, 2015 8:29 AM, "Wolfg ang Weber webercardio@... [amelyachtowners]" <amelyachtowners@...> wrote:
 
 
For your Information. 
This is the answer from Mastervolt concerning the Installation of charger/inverter on Amel 54

"The AC is not connected to the DC terminals inside, the DC is floating to the housing.
however, the AC input is not galphanic isolated from the shore, for this you need a isolation transformer, and create your own ships ground in your boat.
the combi Ultra has an option to switch on a ground relay, this means the neutral in AC output will be connected to the ground in inverter mode automatically. in charger mode (this means there is a AC input like a shore connection, then this relay will be deactivated, because theoretical, the hot and neutral line can be swapped, and you don't want the hot line to be connected to the ground.
our high frequency isolation transformer is 88000355 mass GI 3,5http://www.mastervolt.com/products/mass-gi/mass-gi-35-kva-16a-lightweight/

hope this helps,

best regards, 
Edwin van der Kroon"
 
Any comment ?  Wolfgang Weber SY ELISE  Amel 54 # 162
 
 
 
 



Andrew & Kate Lamb
 

Yes just after I posted my message I looked on some of the US calculators and these as you say seem more conservative. I am not at my boat at the moment but I will certainly take a look at the Amel drawings the next time I am there.

Andrew

Ronpische
SM2k 472
Canet en Roussillion, France



From: amelyachtowners@... [mailto:amelyachtowners@...]
Sent: Wednesday, November 18, 2015 3:59 PM
To: amelyachtowners@...
Subject: Re: [Amel Yacht Owners] Re: Shore Power Configuration


Thanks Andrew, I checked the European wire manufacturers out there and they all seem to indicate that 4mm2 wire is good for up to 32A single phase, so I think you are correct on adequacy in design. I think the US NEC is just more conservative, hence my concern.

I will retain my 32A breaker, but I still would like to find out why my Amel factory electrical schematics indicate a 16 amp 230V circuit breaker. It seems you have a 32A breaker, as do I.

What shore power inlet breaker rating is shown on your Amel drawings?

Thanks,
Jamie


On Wednesday, November 18, 2015 9:46 AM, "Andrew Lamb andrew.lamb@...<mailto:andrew.lamb@...> [amelyachtowners]" <amelyachtowners@...<mailto:amelyachtowners@...>> wrote:


We have a total run of somewhere between 15-20 meters (internal cabling + shore power cable) of twin and earth 4mm2 cross section double insulated cable from the shore power to the 32A circuit breaker in the engine room, then onto the 7.5KW rated isolation transformer. All the online and offline calculators/calculations that I have done seem to suggest that this is adequate.

Andrew

Ronpische
SM2k 472
Canet en Roussillion, France



From: amelyachtowners@...<mailto:amelyachtowners@...> [mailto:amelyachtowners@...]
Sent: Wednesday, November 18, 2015 3:23 PM
To: amelyachtowners@...<mailto:amelyachtowners@...>
Subject: Re: [Amel Yacht Owners] Re: Shore Power Configuration


Bill, thanks for the feedback. Trust me, I am not trying to question what Amel did, as I am sure they have been installing safe and effective electrical systems in their boats. And I also agree that I do not want to "de-Amel" my boat. I like it essentially the way it is.[*:) happy]

But I do have some concerns that my Amel 54 may not be configured as Amel intended, and what I have is definitely not safe. I was hoping to see what others have in their shore power systems to see if I have the right setup. Right now I have a single 32A/230V Hubbel shore power inlet coupled to a 32A/230V circuit breaker in the lazarette feeding my shore power line to the automatic transfer switch in the engine room. The Amel electrical schematics I have indicate there should be a 16A/230V breaker for the 50Hz feeder and also a 32A breaker for a 120V/60Hz feeder with a step-up transformer. I do not have the 16A breaker or the transformer. I am concerned about the possibility that someone may connect my shore power inlet to a 230V or 240V connection (which is what you have to do of course whether in Europe or the US) but then try to run everything in the boat. That would overload my 4mm2 wiring.

I certainly am not immune to making mistakes, but I do think I am looking at this correctly.[*:) happy] I am an electrical engineer, so right or wrong I have based my shore power assessments on US National Electrical Code rules. Your approach to determining wire size based on voltage and voltage drop also can be used, but is only really appropriate for DC wiring and not higher voltage AC systems (whether they are 120V or 230V), where voltage drop is not a concern in a house or boat. Voltage drop is only important if you are looking at DC circuits (where we are dealing with 12 or 24 volts).

Respectfully, I must also point out a few issues with your numbers. 4mm2, commonly available in Europe, is a cross-sectional measurement of the wire and not the diameter or circumference. It is the equivalent of a US Wire Gauge Size 11 per the conversion tables. I can see how you might have equated it to a 6 AWG. Since 11 gauge wire is not commonly available in the US, you would have to use 12 gauge wire to be safe.

Current through the wire is the issue and not voltage or frequency. 12 gauge wire (or 4mm2) on any AC circuit (less than 600 volts) is good for up to a 20A breaker and a maximum of 16 amps of continuous current at either 120V or 230V. If you connect a European 230V (or US 240V) power source to a 32A breaker (as I have), the breaker would allow a huge current (up to about 30 amps before tripping) to pass through my 4mm2 wire. In order to handle that much current, I would need to replace the wiring with 6mm2 wire (or 10 AWG in the US). i do not want to do that, as I agree with you that Amel clearly planned for 4mm2 wiring on the 230V/50Hz shore power feeder, and hence the rationale for a 16A circuit breaker. Also I think you are correct that the vast majority of power systems available throughout Europe are indeed 16A rather than 32A.

Those are the reasons why I think the circuit breaker I have is wrong and I should degrade it to 16 amps at 230V. Of course, that would limit my power capacity, but I think that is what Amel would have installed. What size shore power connector and circuit breaker do you have?

Thanks,
Jamie Wendell
s/v Phantom Amel 54


On Wednesday, November 18, 2015 3:59 AM, "'Bill & Judy Rouse' yahoogroups@...<mailto:yahoogroups@...> [amelyachtowners]" <amelyachtowners@...<mailto:amelyachtowners@...>> wrote:


Jaimie,

I think that you are incorrect on required wire size. How did you calculate that it is wrong? Based on: Wire Circular mils =2 x ρ x I x L / (%Allowable Voltage drop of source voltage)

4mm = 6 gauge...and 6 gauge is adequate for 230VAC 50htz for 200+ foot length at 3%Allowable Voltage drop.

Is it possible that you have made a mistake? Or, is it possible that your calculations of wire size are based on 110VAC common to the USA?

Also, I would assume that if Amel installed a 16 amp breaker in the lazarette that they would have used 16 amps for a reason...maybe because the vast majority of the 230VAC 50htz shore power connection in Europe and around the world happen to be 16 amp. There are some marinas with a 32 amp option, but not many. So, it is highly likely that the 16 amp breaker was intentional. We happen to be plugged into 230VAC 50htz 32 amp shore power now, but in this new marina, the 32 amp plug that we are using is the only one on our pontoon...30 other boats are plugged into 16 amps.

A word of advice to you. The last person you should doubt in terms of Amel systems design is Amel. And the last thing that you want to do with an Amel is to Un-Amel your Amel.

Also, I sent you a private message.

Bill
BeBe #387



On Tue, Nov 17, 2015 at 4:24 PM, James Wendell ms42phantom54@...<mailto:ms42phantom54@...> [amelyachtowners] <amelyachtowners@...<mailto:amelyachtowners@...>> wrote:

That definitely helps. So in your case all shore power feeds through the Mass GI 3.5, presumably protected by a 16A circuit breaker in the lazarette? Is that the size breaker you have?

I have a 32A breaker in the lazarette, which is too large for the 4mm2 wire Amel installed, and it would not safely protect that size isolation transformer.

I plan to change that to a 16A breaker and use a similarly- sized isolation transformer like yours (I am using the Victron 3.6 unit). I just want to be sure that the breaker doesn't trip all the time if AC loads exceed the 16 amps permitted.

Thanks,
Jamie Wendell
s/v Phantom Amel 54


On Tuesday, November 17, 2015 8:29 AM, "Wolfg ang Weber webercardio@...<mailto:webercardio@...> [amelyachtowners]" <amelyachtowners@...<mailto:amelyachtowners@...>> wrote:


For your Information.
This is the answer from Mastervolt concerning the Installation of charger/inverter on Amel 54

"The AC is not connected to the DC terminals inside, the DC is floating to the housing.
however, the AC input is not galphanic isolated from the shore, for this you need a isolation transformer, and create your own ships ground in your boat.
the combi Ultra has an option to switch on a ground relay, this means the neutral in AC output will be connected to the ground in inverter mode automatically. in charger mode (this means there is a AC input like a shore connection, then this relay will be deactivated, because theoretical, the hot and neutral line can be swapped, and you don't want the hot line to be connected to the ground.
our high frequency isolation transformer is 88000355 mass GI 3,5http://www.mastervolt.com/products/mass-gi/mass-gi-35-kva-16a-lightweight/

hope this helps,

best regards,
Edwin van der Kroon"

Any comment ? Wolfgang Weber SY ELISE Amel 54 # 162


Bill & Judy Rouse <yahoogroups@...>
 

Jamie,

BeBe SM #387 does not have an isolation transformer and does not have a breaker before the breaker on the side of the 220VAC electrical panel. That is a GFC breaker rated at 32 amps.

I am not an electrical engineer, so I test electrical devices by touching them to see how hot are charged they are. This has served me well, but I have lost a few brain cells doing this...maybe I'll buy a Fluke one of these days.

Good luck on your project, and don't use the touch-test to test for a load...that only works for us IEs.

Bill
Bebe 387

On Wed, Nov 18, 2015 at 3:06 PM, Andrew Lamb andrew.lamb@... [amelyachtowners] <amelyachtowners@...> wrote:
 

Yes just after I posted my message I looked on some of the US calculators and these as you say seem more conservative. I am not at my boat at the moment but I will certainly take a look at the Amel drawings the next time I am there.

 

Andrew

 

Ronpische

SM2k 472

Canet en Roussillion, France

 

 

 

From: amelyachtowners@... [mailto:amelyachtowners@...]
Sent: Wednesday, November 18, 2015 3:59 PM


To: amelyachtowners@...
Subject: Re: [Amel Yacht Owners] Re: Shore Power Configuration

 

 

Thanks Andrew, I checked the European wire manufacturers out there and they all seem to indicate that 4mm2 wire is good for up to 32A single phase, so I think you are correct on adequacy in design. I think the US NEC is just more conservative, hence my concern.

 

I will retain my 32A breaker, but I still would like to find out why my Amel factory electrical schematics indicate a 16 amp 230V circuit breaker. It seems you have a 32A breaker, as do I.

 

What shore power inlet breaker rating is shown on your Amel drawings?

 

Thanks,

Jamie

 

 

On Wednesday, November 18, 2015 9:46 AM, "Andrew Lamb andrew.lamb@... [amelyachtowners]" <amelyachtowners@...> wrote:

 

 

We have a total run of somewhere between 15-20 meters (internal cabling + shore power cable)  of twin and earth 4mm2 cross section double insulated cable from the shore power to the 32A circuit breaker in the engine room, then onto the 7.5KW rated isolation transformer. All the online and offline calculators/calculations that I have done seem to suggest that this is adequate.

 

Andrew

 

Ronpische

SM2k 472

Canet en Roussillion, France

 

 

 

From: amelyachtowners@... [mailto:amelyachtowners@...]
Sent: Wednesday, November 18, 2015 3:23 PM
To: amelyachtowners@...
Subject: Re: [Amel Yacht Owners] Re: Shore Power Configuration

 

 

Bill, thanks for the feedback. Trust me, I am not trying to question what Amel did, as I am sure they have been installing safe and effective electrical systems in their boats. And I also agree that I do not want to "de-Amel" my boat. I like it essentially the way it is.

 

But I do have some concerns that my Amel 54 may not be configured as Amel intended, and what I have is definitely not safe. I was hoping to see what others have in their shore power systems to see if I have the right setup. Right now I have a single 32A/230V Hubbel shore power inlet coupled to a 32A/230V circuit breaker in the lazarette feeding my shore power line to the automatic transfer switch in the engine room. The Amel electrical schematics I have indicate there should be a 16A/230V breaker for the 50Hz feeder and also a 32A breaker for a 120V/60Hz feeder with a step-up transformer. I do not have the 16A breaker or the transformer. I am concerned about the possibility that someone may connect my shore power inlet to a 230V or 240V connection (which is what you have to do of course whether in Europe or the US) but then try to run everything in the boat. That would overload my 4mm2 wiring.

 

I certainly am not immune to making mistakes, but I do think I am looking at this correctly. I am an electrical engineer, so right or wrong I have based my shore power assessments on US National Electrical Code rules. Your approach to determining wire size based on voltage and voltage drop also can be used, but is only really appropriate for DC wiring and not higher voltage AC systems (whether they are 120V or 230V), where voltage drop is not a concern in a house or boat. Voltage drop is only important if you are looking at DC circuits (where we are dealing with 12 or 24 volts).

 

Respectfully, I must also point out a few issues with your numbers. 4mm2, commonly available in Europe, is a cross-sectional measurement of the wire and not the diameter or circumference. It is the equivalent of a US Wire Gauge Size 11 per the conversion tables. I can see how you might have equated it to a 6 AWG. Since 11 gauge wire is not commonly available in the US, you would have to use 12 gauge wire to be safe.

 

Current through the wire is the issue and not voltage or frequency. 12 gauge wire (or 4mm2) on any AC circuit (less than 600 volts) is good for up to a 20A breaker and a maximum of 16 amps of continuous current at either 120V or 230V. If you connect a European 230V (or US 240V) power source to a 32A breaker (as I have), the breaker would allow a huge current (up to about 30 amps before tripping) to pass through my 4mm2 wire. In order to handle that much current, I would need to replace the wiring with 6mm2 wire (or 10 AWG in the US). i do not want to do that, as I agree with you that Amel clearly planned for 4mm2 wiring on the 230V/50Hz shore power feeder, and hence the rationale for a 16A circuit breaker. Also I think you are correct that the vast majority of power systems available throughout Europe are indeed 16A rather than 32A.

 

Those are the reasons why I think the circuit breaker I have is wrong and I should degrade it to 16 amps at 230V. Of course, that would limit my power capacity, but I think that is what Amel would have installed. What size shore power connector and circuit breaker do you have?

 

Thanks,

Jamie Wendell

s/v Phantom Amel 54

 

 

On Wednesday, November 18, 2015 3:59 AM, "'Bill & Judy Rouse' yahoogroups@... [amelyachtowners]" <amelyachtowners@...> wrote:

 

 

Jaimie,

 

I think that you are incorrect on required wire size. How did you calculate that it is wrong? Based on: Wire Circular mils =2 x ρ x I x L / (%Allowable Voltage drop of source voltage) 

 

4mm = 6 gauge...and 6 gauge is adequate for 230VAC 50htz for 200+ foot length at 3%Allowable Voltage drop.

 

Is it possible that you have made a mistake? Or, is it possible that your calculations of wire size are based on 110VAC common to the USA?

Also, I would assume that if Amel installed a 16 amp breaker in the lazarette that they would have used 16 amps for a reason...maybe because the vast majority of the 230VAC 50htz shore power connection in Europe and around the world happen to be 16 amp. There are some marinas with a 32 amp option, but not many. So, it is highly likely that the 16 amp breaker was intentional. We happen to be plugged into 230VAC 50htz 32 amp shore power now, but in this new marina, the 32 amp plug that we are using is the only one on our pontoon...30 other boats are plugged into 16 amps.

 

A word of advice to you. The last person you should doubt in terms of Amel systems design is Amel. And the last thing that you want to do with an Amel is to Un-Amel your Amel.

 

Also, I sent you a private message.

 

Bill

BeBe #387

 

 

 

On Tue, Nov 17, 2015 at 4:24 PM, James Wendell ms42phantom54@... [amelyachtowners] <amelyachtowners@...> wrote:

 

That definitely helps. So in your case all shore power feeds through the Mass GI 3.5, presumably protected by a 16A circuit breaker in the lazarette? Is that the size breaker you have?

 

I have a 32A breaker in the lazarette, which is too large for the 4mm2 wire Amel installed, and it would not safely protect that size isolation transformer.

 

I plan to change that to a 16A breaker and use a similarly- sized isolation transformer like yours (I am using the Victron 3.6 unit). I just want to be sure that the breaker doesn't trip all the time if AC loads exceed the 16 amps permitted.

 

Thanks,

Jamie Wendell

s/v Phantom Amel 54

 

 

On Tuesday, November 17, 2015 8:29 AM, "Wolfg ang Weber webercardio@... [amelyachtowners]" <amelyachtowners@...> wrote:

 

 

For your Information. 

This is the answer from Mastervolt concerning the Installation of charger/inverter on Amel 54

"The AC is not connected to the DC terminals inside, the DC is floating to the housing.
however, the AC input is not galphanic isolated from the shore, for this you need a isolation transformer, and create your own ships ground in your boat.
the combi Ultra has an option to switch on a ground relay, this means the neutral in AC output will be connected to the ground in inverter mode automatically. in charger mode (this means there is a AC input like a shore connection, then this relay will be deactivated, because theoretical, the hot and neutral line can be swapped, and you don't want the hot line to be connected to the ground.
our high frequency isolation transformer is 88000355 mass GI 3,5http://www.mastervolt.com/products/mass-gi/mass-gi-35-kva-16a-lightweight/

hope this helps,

best regards, 
Edwin van der Kroon"

 

Any comment ?  Wolfgang Weber SY ELISE  Amel 54 # 162